I just got a second wen inverter generator 2250watts, both are still in the box, its one of those enclosed type, wen website has them for 385 right now. anyway, i saw on the front it has a knob or something for ground wire, does it need to have a ground wire to run my chest freezer? thanks....
Plant Gadget Machine Personal protective equipment Font
 

·
Registered
Joined
·
9,160 Posts
No. Grounding to an electrode such as a ground rod provides no low-resistant path for a ground-fault to operate an overcurrent device.

Proper grounding is accomplished through the same wiring method used to power the freezer.
 

·
Super Moderator
Joined
·
9,191 Posts
Not sure what that means, Back Pack Hack????? If the freezer is disconnected from the home's power outlet, how is anything grounded?
 

·
Registered
Joined
·
108 Posts
If you don't want to be shocked when you touch the frig, best to add a ground to the case of the generator. When the generator is connecter to only the frig even with a 3 wire cord there is no connection to earth ground.
 

·
Registered
Joined
·
9,160 Posts
Earth grounding does zip for shock protection. The earth has such a high resistance it WILL NOT cause a breaker/fuse to open in case of a fault.

In fact, here's what 250.4(A)(5) of the National Electrical Code says:

(5) Effective Ground-Fault Current Path. Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a low-impedance circuit facilitating the operation of the overcurrent device or ground detector for high-impedance grounded systems. It shall be capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source. The earth shall not be considered as an effective ground-fault current path .
Pay close attention to the last sentence.
 

·
Registered
Joined
·
755 Posts
You can never go wrong by grounding electrical units to a dedicated ground rod (preferably copper coated and 6' deep) but don't really think it's necessary in your case. But if there's a special hook up on the unit for a ground then why not?
 

·
Registered
Joined
·
9,160 Posts
.... But if there's a special hook up on the unit for a ground then why not?
Those are for those cases when you use the genny to energize a building's existing wiring system. Again, if you're using cords, then grounding to earth is a waste of time and money.
 